Set up UPS on Ubuntu Server
Hi,
I just got a UPS Eaton Powerware 5110 1000A that I'd like to plug into my Ubuntu Server 12.04 LTS. I have done this with machine running on Windows XP SP3. However, as I'm quite familiar but not too savvy with Linux machine, I'm not sure if I should set it up using the CD that comes with the UPS or from the following link that teaches how to install 5110 on Ubuntu https://help.ubuntu.com/community/Po...5110UPSin12.04 Any help would be greatly appreciated. Thank you |
Eaton has their own, propriatary management software which come bundled with their UPS units and can be downloaded from their web site as well.
The link points to an article describing how monitor a 5110 using Network UPS Tools, a free, open-source power management tool. You may use either program to manage your UPS. |
Thank you for your reply.
Sorry for the late reply. I decided to follow the steps from the link mentioned in my opening thread which is https://help.ubuntu.com/community/Po...5110UPSin12.04 1. install nut by "apt-get install nut" <...> However, I was stuck at the point where I need to edit the following file: gksudo gedit /etc/udev/rules.d/99_nut-serialups.rules Well, there is no such file as 99_nut-serialups.rules under /etc/udev/rules.d. I'm not sure if this procedure is designed for a normal Ubuntu desktop 12.04, not for Server 12.04. Any help would be greatly appreciated. Thank you |
Quote:
|
Thank you for your reply.
No, I didn't. I can try to create one and see what happens. Thank you very much |
Thank you for your reply.
I have been testing it for a couple of days consecutively because the first and the second days did not work as I wanted it to. What happened was it did not shut down immediately when the power went out although I had set "SHUTDOWNCMD" to "/sbin/shutdown -h now". I actually waited for a couple of minutes and it still did not shut down. I did not get any message that's indicating it's going to shutdown in x minutes or something at all. This is how I installed it based on the link I mentioned in my opening post. Installing: apt-get install nut Editing /etc/nut/ups.conf : [Powerware5110] driver = bcmxcp_usb port = auto I use port=auto Since I use USB cable to connect my Powerware 5110 to my Ubuntu server 12.04 LTS I created a file /etc/udev/rules.d/99_nut-serialups.rules and add the following: KERNEL=="ttyS0", GROUP="nut" Then, Start: $ sudo udevadm control --reload-rules $ sudo udevadm trigger $ sudo upsdrvctl start Network UPS Tools - UPS driver controller 2.4.6 Network UPS Tools - BCMXCP UPS driver 0.25 (2.4.6) USB communication subdriver 0.19 Editing /etc/nut/upsd.conf by adding and save: ACL all 0.0.0.0/0 ACL localhost 127.0.0.1/32 ACCEPT localhost REJECT all Editing /etc/nut/upsd.users by adding and save: [mysystemuser] password = __YOUR_PASSWORD_HERE__ allowfrom = localhost upsmon master Editing /etc/nut/upsmon.conf This, I'm not sure if I did it right. I actually commented those existing variables in every lines and add the followings to the last line: MONITOR Powerware5110@localhost 1 mysystemuser __YOUR_PASSWORD_HERE__ master POWERDOWNFLAG /etc/killpower SHUTDOWNCMD "/sbin/shutdown -h now" and save. then, change permissions sudo chown root:nut /etc/nut/* sudo chmod 640 /etc/nut/* Editing /etc/default/nut START_UPSD=yes START_UPSMON=yes Editing /etc/nut/nut.conf MODE=standalone Start nut: sudo /etc/init.d/nut start Then, did sudo upsc Powerware5110 and received the following: ambient.temperature.high: 137 ambient.temperature.low: 34 battery.charge.low: 22 battery.voltage: 26.9 device.mfr: Eaton device.model: POWERWARE UPS 1000i device.serial: device.type: ups driver.name: bcmxcp_usb driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.6.3 driver.version.internal: 0.25 input.frequency: 50.1 input.frequency.high: 55 input.frequency.low: 45 input.frequency.nominal: 50 input.transfer.boost.high: 216 input.transfer.high: 280 input.transfer.low: 186 input.transfer.trim.low: 260 input.voltage: 246 input.voltage.nominal: 240 output.current: 0.6 output.current.nominal: 2.5 output.frequency: 50.1 output.phases: 1 output.voltage: 246 output.voltage.nominal: 240 ups.beeper.status: enabled ups.firmware: Cont:00.50 Inve:01.50 ups.load: 24.0 ups.mfr: Eaton ups.model: POWERWARE UPS 1000i ups.power.nominal: 1000 ups.serial: ups.status: OL So it seems like everything is working fine. When I deliberately switched my main power off, I could hear my powerware 5110 start beeping and saw the "ups.status: ALARM OB". So everything looks fine. But it didn't turn off the server right away. WOndering if you could advice me where I did it wrong that might cause it not to work properly. Thank you |
Normally, nut will not initiate shutdown until the UPS reports a low battery condition. If that's not wat you want, take a look at man upssched.
|
Thank you for your reply.
Yes, you're absolutely right about using the upssched. After reading the upssched manual as suggested, it now does what I want it to do that is wait for 60 secs before shutting down. It's all good now Thank you for your help |