nibraz 07-10-2012 10:23 AM

2 power cords?
 
I got a dell r610 server, there are 2 power input, do I use them both? i mean do i plug two power cords to those 2 ports?

TenTenths 07-10-2012 10:26 AM

You will find that the server will run on only 1, the other is a redundant backup. My personal preference is to have one PSU in to the mains and another into a UPS. Alternatively have them both in to separate UPSs that are on separate circuit breakers.

nibraz 07-10-2012 11:22 AM

Quote:

Originally Posted by TenTenths (Post 4724023)
You will find that the server will run on only 1, the other is a redundant backup. My personal preference is to have one PSU in to the mains and another into a UPS. Alternatively have them both in to separate UPSs that are on separate circuit breakers.

Thats great. Thanks!

jefro 07-10-2012 08:26 PM

We plug both as per owners manual. It may be dangerous to use dual circuit breakers and is against code in some locations unless it is marked as a dual input. In a normal rack the rack is on a single breaker or room ups. The bottom of the rack may have two ups's and that would be a choice for each psu plug to end at.

TenTenths 07-11-2012 03:50 AM

My suggestion comes from personal experience, we had a rack where there were two UPSs and one "direct" mains PDU. Some of the servers had both inputs on UPSs (separate) and some servers (the ones I commissioned!) had one input in to a UPS and the other into the "direct" mains PDU.

Mains service failed, so all servers stayed "up" as they had at least one input on the UPSs.
Generator kicks in, so "direct" mains is restored, so far, so good, everyone is happy :)
Mains service is restored, however during this process the circuit breaker protecting the 16Amp circuit to the UPSs "throws", as a result the UPSs aren't being supplied with mains.
Everything is fine for 45 minutes until the UPSs run dry.
So, servers that had both input off (separate!) UPSs - down.
Servers with one input off UPS and one off mains - up.

So if you have the budget/space/facilities try and split your server power input strategy to mitigate single point of failure. In that case, the SPF was that both UPSs were off the same mains feed and therefore an SPF existed at the circuit breaker.

We were fortunate that there were other separate 16Amp feeds in to that room so the servers (and switches) ended up with one in the mains and one in the UPSs.