How do you determine how much AC for a server room?


I'm trying to build out or new machine room. I'm not sure how to figure how much cooling capacity I need for the number of machines I have. Is there some sort of formula....? number of amps consumed per hour * voltage = X btu? Someting like that?

I currently have about 50 machines that will be in the server room ranging from dual 1GHz PIII to dual 3GHz Xeon. Some 4U, some 2U, most 1U... those and a couple UPSs. The AC unit I have is either a 1.5 ton or 2 ton unit (I don't know what that means as far as BTUs go?). I just want to be sure if that's enough, or if I'll need bigger, or possibly 2 of these. etc.
 
Old 10-03-2006, 04:35 AM   #2
michaelk
Moderator
 
Registered: Aug 2002
Posts: 25,680

Rep: Reputation: 5894Reputation: 5894Reputation: 5894Reputation: 5894Reputation: 5894Reputation: 5894Reputation: 5894Reputation: 5894Reputation: 5894Reputation: 5894Reputation: 5894
A "ton of refrigeration" is defined as the cooling power of one short ton (2000 pounds or 907 kilograms) of ice melting in a 24-hour period. This is equal to 12,000 BTU per hour, or 3517 watts.

I found this link which seems like a good starting point.
http://www.periphman.com/computer-ro...lculator.shtml

However, IMO it is just a WAG and you should get professional help designing the room for max efficiency.

P.S. All disclaimers apply

Last edited by michaelk; 10-03-2006 at 04:44 AM.
 
Old 10-03-2006, 01:02 PM   #3
BrianK
Senior Member
 
Registered: Mar 2002
Location: Los Angeles, CA
Distribution: Debian, Ubuntu
Posts: 1,334

Original Poster
Rep: Reputation: 51
Quote:
Originally Posted by michaelk
A "ton of refrigeration" is defined as the cooling power of one short ton (2000 pounds or 907 kilograms) of ice melting in a 24-hour period. This is equal to 12,000 BTU per hour, or 3517 watts.

I found this link which seems like a good starting point.
http://www.periphman.com/computer-ro...lculator.shtml

However, IMO it is just a WAG and you should get professional help designing the room for max efficiency.

P.S. All disclaimers apply
Good info, thanks for that.

I could call a professional, but I'm trying to do this on a budget & through a mistake by the building owner, am getting the AC units for free - so the less outside help required, the better.

That said, I may call a professional.

If anyone else has any ideas, feel free to chime in.
 
Old 10-03-2006, 05:51 PM   #4
J.W.
LQ Veteran
 
Registered: Mar 2003
Location: Boise, ID
Distribution: Mint
Posts: 6,642

Rep: Reputation: 87
Moved: This thread is more suitable in General and has been moved accordingly to help your thread/question get the exposure it deserves.

Mod note: This is not technically a Linux question, so it's off to General
 
Old 10-03-2006, 10:03 PM   #5
twilli227
Member
 
Registered: May 2003
Location: S.W. Ohio
Distribution: Ubuntu, OS X
Posts: 760

Rep: Reputation: 30
Hate to tell you this, but I don't think even a 2 ton unit will take care of your situation. We have a small server room with less than 50 servers, but also has UPS's in there and we have 3 - 5 ton units. If one unit can't keep up, then the second unit kicks in, and if two can't keep up, then the third unit kicks in. Our main computer room wich has more than 50 servers and UPS's has a 30 ton unit. On hot days, that unit is doing all it can to keep the room cool. They finally bought a backup unit just in case the main one goes out or it can't keep it cool enough.
As suggested, I would get advice from a couple of professionals. There are a number of things to look at, heat output of all of your machines, future additions to the number of machines you might add, cooling loss out of the server room, etc.
Unfortunately it will cost some bucks, but if you don't do it right, think what will happen if and when your cooling system can't keep up or worse, goes out on the hottest day of the year.
Good luck and I hope it works out for you.
 
  


Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off



Similar Threads
Thread Thread Starter Forum Replies Last Post
Chat Room? plisken LQ Suggestions & Feedback 6 11-26-2005 09:47 AM
determine load on a linux web server sandeep2005 Linux - General 1 10-22-2005 02:41 PM
no more room in partition! jnev Linux - General 7 09-21-2005 08:58 PM
More Room on / Difficult Linux - Newbie 15 07-10-2002 03:44 PM
Chat room LinuzRulz General 11 06-07-2002 08:26 AM

LinuxQuestions.org > Forums > Non-*NIX Forums > General

All times are GMT -5. The time now is 09:38 AM.

Main Menu
Advertisement
My LQ
Write for LQ
LinuxQuestions.org is looking for people interested in writing Editorials, Articles, Reviews, and more. If you'd like to contribute content, let us know.
Main Menu
Syndicate
RSS1  Latest Threads
RSS1  LQ News
Twitter: @linuxquestions
Open Source Consulting | Domain Registration