2 power cords?


I got a dell r610 server, there are 2 power input, do I use them both? i mean do i plug two power cords to those 2 ports?
 
Old 07-10-2012, 10:26 AM   #2
TenTenths
Senior Member
 
Registered: Aug 2011
Location: Dublin
Distribution: Centos 5 / 6
Posts: 1,244

Rep: Reputation: 394Reputation: 394Reputation: 394Reputation: 394
You will find that the server will run on only 1, the other is a redundant backup. My personal preference is to have one PSU in to the mains and another into a UPS. Alternatively have them both in to separate UPSs that are on separate circuit breakers.
 
Old 07-10-2012, 11:22 AM   #3
nibraz
Member
 
Registered: Oct 2008
Posts: 98

Original Poster
Rep: Reputation: 16
Quote:
Originally Posted by TenTenths View Post
You will find that the server will run on only 1, the other is a redundant backup. My personal preference is to have one PSU in to the mains and another into a UPS. Alternatively have them both in to separate UPSs that are on separate circuit breakers.
Thats great. Thanks!
 
Old 07-10-2012, 08:26 PM   #4
jefro
Guru
 
Registered: Mar 2008
Posts: 10,246

Rep: Reputation: 1255Reputation: 1255Reputation: 1255Reputation: 1255Reputation: 1255Reputation: 1255Reputation: 1255Reputation: 1255Reputation: 1255
We plug both as per owners manual. It may be dangerous to use dual circuit breakers and is against code in some locations unless it is marked as a dual input. In a normal rack the rack is on a single breaker or room ups. The bottom of the rack may have two ups's and that would be a choice for each psu plug to end at.
 
Old 07-11-2012, 03:50 AM   #5
TenTenths
Senior Member
 
Registered: Aug 2011
Location: Dublin
Distribution: Centos 5 / 6
Posts: 1,244

Rep: Reputation: 394Reputation: 394Reputation: 394Reputation: 394
My suggestion comes from personal experience, we had a rack where there were two UPSs and one "direct" mains PDU. Some of the servers had both inputs on UPSs (separate) and some servers (the ones I commissioned!) had one input in to a UPS and the other into the "direct" mains PDU.

Mains service failed, so all servers stayed "up" as they had at least one input on the UPSs.
Generator kicks in, so "direct" mains is restored, so far, so good, everyone is happy
Mains service is restored, however during this process the circuit breaker protecting the 16Amp circuit to the UPSs "throws", as a result the UPSs aren't being supplied with mains.
Everything is fine for 45 minutes until the UPSs run dry.
So, servers that had both input off (separate!) UPSs - down.
Servers with one input off UPS and one off mains - up.

So if you have the budget/space/facilities try and split your server power input strategy to mitigate single point of failure. In that case, the SPF was that both UPSs were off the same mains feed and therefore an SPF existed at the circuit breaker.

We were fortunate that there were other separate 16Amp feeds in to that room so the servers (and switches) ended up with one in the mains and one in the UPSs.
 
  


Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
[SOLVED] Power Supply Cords - Did They Change? MBA Whore Linux - Hardware 10 08-01-2009 08:22 PM
power company idiots cut power while system was on, now hangs at boot with # prompt shroomy_bee Linux - Newbie 10 07-04-2008 12:12 AM
using my desktop without power cords gabeyg General 15 09-26-2007 04:35 PM
LXer: Linux Networx partners with CEI to power 2X visualization power of ... LXer Syndicated Linux News 0 04-26-2006 03:03 AM
Case to Mobo Cords with NF7-S CoLuGo Linux - Hardware 3 10-16-2003 03:07 PM


All times are GMT -5. The time now is 11:05 AM.

Main Menu
My LQ
Write for LQ
LinuxQuestions.org is looking for people interested in writing Editorials, Articles, Reviews, and more. If you'd like to contribute content, let us know.
Main Menu
Syndicate
RSS1  Latest Threads
RSS1  LQ News
Twitter: @linuxquestions
identi.ca: @linuxquestions
Facebook: linuxquestions Google+: linuxquestions
Open Source Consulting | Domain Registration